Hi to all Heating and Vent. With A/C in RAVE K4 page 1. There is a table temperature / resistance does any one know if this table cover both sensors, at the moment I’m testing the Evaporator sensor but not getting the reading shown, if I put the sensor in the freezer at -22 it reads 65.3k in the fish tank at 20o C it reads 6.0k but if I go by the table it should read 94.5k at -20oC and at 20oC it should read 12.5k
I’ve already ordered a new replacement but don’t want to replace it if its ok, can anyone confirm if the table applies to both sensors. Best Regards sillyboy